CONTROL VALVE
CONTROL VALVE
How does a flow control valve characteristics changes if erected in reverse diriection. what effects will it have on it's capacity
RE: CONTROL VALVE
1 - If valve is feeding into an open downstream system where system resistance curve is low, if the valve is closing tight against very low downstream pressure, if there is a high pressure differential across the valve, then the valve closing speed curve will lengthen and flatten out (longer close time, more linear closing rate). All this is due to the fact that the ratio between entry and exit "chambers" is different based on what direction the water flows in. High differential pressure across a diaphragm valve can cause the diaphragm supported disc to collapse against the seat at the end of the stroke because hdraulic support under the digphragm from downstream pressure is lost "exponentially" on an open system.
2 - As far as modulating the valve will behave similar in either direction with differences large and small depending on system conditions.
Describe the application and system conditions, show us the system curve if you have it.
PUMPDESIGNER
RE: CONTROL VALVE
RE: CONTROL VALVE
Br
B
RE: CONTROL VALVE
RE: CONTROL VALVE
If the above isn't do-able, contact the Manu'f. for the tech data on reverse flow through the valve, if they have it. They will in all probability tell you to reverse the valve.
Godluck.
saxon
RE: CONTROL VALVE
Hope this helps.
saxon