Height of water seal

Height of water seal

Height of water seal

(OP)
Guys
I would like to know the height of water seal required in a floor trap which is subjected to a vacuum pressure of
-50 pa(the trap is located in a lab which is under negative room pressure)

RE: Height of water seal

I can fax a diagram for vacuum service "P" trap design by request: cbb@atlas-stord.com, include fax #

RE: Height of water seal

50 Pa corresponds to 5 mm of water column. That means the given negative pressure can hold a water column of 5 mm height and rest of the water will be drained. Generally the U Seal for floor drains will be of 1.5" to 2". So no problem in your case.

Regards,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources