Surge Arrester Sizing

Surge Arrester Sizing

Surge Arrester Sizing

(OP)
Hello!

What would be the proper or better protection for a substation and distribution system from surges?

Our practice is to use; 72KV and 15KV arresters on the substation high side and low side respectively. Line distribution is protected with 12kv arresters.

A project engineer on a new substation commends that we shall use 60KV rms with 48KV MCOV on the high side. The low side shall be 12KV & 10.2KV MCOV and 10KV, 8.4KV MCOV for line protection.

The project is a 33MVA, 69/13.8 KV, DYn1, 3-phase, 60Hz substation.

The utility is connected at load-end of a 69KV sub-transmission line. Distribution system is UNIGROUNDED.

Thanks in advance.

RE: Surge Arrester Sizing


There may be applicable material in

IEEE C62.22 …Application of Metal-Oxide Surge Arresters…, and
IEEE C62.92.4  …Neutral Grounding in Electrical Utility Systems, Part IV—Distribution.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources