DC Motor Starting amps

DC Motor Starting amps

DC Motor Starting amps

(OP)
My question is, the amps on the nameplate of a DC motor,is that what it runs at? and do the amps spike on start up of that motor?Thanks in advance.

RE: DC Motor Starting amps

Hi, the amperage on the name plate is FLA(Full load amps), the amperage while running can very depending on the load.  If the current exceeds the FLA, then you could possibly have the wrong size motor, or you have a mechanical falure somewhere in the system.

Yes, on start up the current will "spike up", this is called inrush current and it will be higher than the name plate FLA.

Best Regards
Buhsman

RE: DC Motor Starting amps

Suggestion: The DC motor starting amps depend on the motor starting arrangement. The motor starting inrush current may be substantially reduced by soft starting devices.
The motor nameplate or full load rated current is not supposed to be exceeded to protect the motor against damages and premature aging.

RE: DC Motor Starting amps

the nameplate amps is the full load rated, and is also accompanied by a service factor.
The load and the applied voltage( and accel/ decell time of a drives ramp will determine the "spike amps"
The  current will become larger the faster you wish to accel the motor, ...or the heavier you load it. Most Dc motors can take 200% Ia for about 60 sec, but it will depend on the commutation ability of the motor, and brush loading. As long as there is no sparking , you are " black" and within the overload rating of the motor.
THIS DOES NOT INCLUDE THE THERMAL LIMITS...and you must not do it for very long.
It is not uncommon for rolling mil and crane motors to have curent limit and the Timed overloads set upwards of 200%-250% rated amps.It all depends on the motor, application , drive rating, and cooling.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources