Watts to BTU calculation
Looking for the calculation which converts watts per sqare foot, to BTU then to refrigeration tonnage. Any help would appreciated.
RE: Watts to BTU calculation
1 watt per square foot is approximately 3.14 btu per square foot
Thanks!!
please note that conversation factor is 3.44 (not 3.14)
Isn't 3.413 Unless my Teachers are wrong... Which is entirely possible.
A very good conversion program that is free to use and distribute:
http://www.joshmadison.com/software/
lists the coversion as 1 watt-hour = 3.412142 BTU.
Gentlemen you are forgetting the basics here !!!
You can not convert watts/ft2 to BTU because you can't compare power/area with energy
Steven van Els
SAvanEls@cq-link.sr
In the UK we have gone through this conversion thing already, so here is typical conversions used
Power
kW -> BTU/hr(x 3412)
Tons Refrigeration -> kW (x 3.517)
Intensity of heat flow rate
BTU/hr square foot -> W/square metre (x 3.155)
Typically for budget cooling load estimating we use 140 W/square metre.