R22 compressor used with R12

R22 compressor used with R12

R22 compressor used with R12

(OP)
Due not known razon it is a water chiller with out its compressor.

The facts are as follow :
Home made or a little shop done.
All presostats are setup for R12 pressures.
High press set point 225 # (pd/sq inch)
Low press set point to control the system 32 #
Low press set point to avoid runing without gas 6#
The suction and discharge pipes have ROTALOC as the ones pertaining to COPELAMETIC.
Air condensed.
Termic relay rated at 5,5 AMP
Voltage 3 x 380V  50 Hz
I have no idea about waterflow .
Output chilled water temp: 4 °C

All seem to be that a 500 series COPELAMETIC or 5Hp.
It was a way of work here to use a R22 compressor but runing it on R12 because to this HP rate a 5HP R22 comp is cheaper than a 4 HP R12 compresor , and in our country there where not any COPELAMETIC Compressor for R12.


My corncern is , what is the rated capacity when any given R22 compressor is run with R12?? .

Thank in advance.


 
 




Pardal

RE: R22 compressor used with R12

(OP)
I DID A MISTAKE .


It should be a COPELAWELD no a COPELAMETIC.

Pardal

RE: R22 compressor used with R12

I did a quick calculation considering 00C evaporating temperature and 30 0C condensing temperature, neglecting subcooling and superheating at condenser and evaporator respectively. The power consumption drops by 4% when used with R12. Compression ratio is almost same for both R12 and R22. But you should change the expansion device.Discharge pressure of 225PSI seems to be quite high.

Regards,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources