GEC CDG14 Overcurrent relay curves
Do you know where I can find the curves of a GEC CDG14 overcurrent relays, or where I can find the B.S. 142:1966 standar?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
GEC CDG14 Overcurrent relay curvesGEC CDG14 Overcurrent relay curves(OP)
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
RE: GEC CDG14 Overcurrent relay curves
check at the Alstom.com web site
acc to page 139 of PRAG ( where you can see the curves) the formula for the extremely inverse curve is t=80/(Isquare-1) where t is op time in sec and I is current (multiple of plug setting)
The formulas in the PRAG that you mention are for electronic/numerical relays.
If you look at the curve for the CDG14, at 5 times the current setting the relay operates in 2.05 seconds.
If you put the same value into the EI formula, the operating time is 3.33 seconds
If you don't have a copy of the PRAG, contact ALSTOM for a copy of the CDG14 publication.
Switchgear/boards/relays/motors
Thread279-13401 for more info