Gas Quality High Btu Swings
Gas Quality High Btu Swings
(OP)
I am trying to identify what is the operating impact of varying Btu in a natual gas fuel source to process or power generating loads. I am talking about swings of 60 - 70 Btu within hours of a day. Please state your concerns and experience with problems if available.





RE: Gas Quality High Btu Swings
RE: Gas Quality High Btu Swings
chemically, the higher Btu gas requires more air (volume) than a lower value for combustion.. I guess for your consideration, you need to make sure that your combustion controls are set up to allow sufficient air for the higher Btu content
RE: Gas Quality High Btu Swings
If it varies too high, I can adjust my fuel ratio controller parameters and keep operating, as long as the plant operator sees the change before the engine goes into detonation and shuts down. If the detonation sensing system fails, then I experience severe engine damage.
If the fuel heat content drops more than 5%, then my fuel system can't supply enough to make full power. Therefore, the plant can't produce rated output. If my power is being sold via contract or is pre-scheduled into the grid for the open market, then I have to buy replacement power. If the market is high, I am going to be real mad.
For either case, I would be on the phone to my GasCo right away to find out what is going on.
Even with pipeline fuel, assuming just under 1000 btu/scf, your 60-70 Btu change would be outside the 5% variance allowed by my engine's fuel system. Your inability to control fuel quality is going to impact your customer negatively, if his system is similar to mine.