Motor Undervoltage Protection

Motor Undervoltage Protection

Motor Undervoltage Protection

(OP)
In a transient stability study I noticed that induction motors are modeled with undervoltage protection. The model shows a voltage pick-up setting of 0.60 pu and a time delay of 30 cycles. Do these values seem right? What is the range of typical settings? Any info would be greatly appreciated.

Michael Sidiropoulos

RE: Motor Undervoltage Protection

The first question to ask is what is the load torque that is required to start the motor and load rolling.
The next question is what does the damage curve of the motor look like and what is the maximum time that the motor can stand to get the load rolling. With this information and some homework you should be able to calculate the settings of the protective relay.

RE: Motor Undervoltage Protection

(OP)
The stability model that I referred to above shows dynamic data for hundreds of motors around the system, all with the same voltage setting of 0.60 pu and time delay of 30 cycles. I find the uniform modeling surprising but it's done, I guess, for simplicity or lack of specific data. My question is: are these settings within the range of typical values? Are they reasonable?

Michael Sidiropoulos

RE: Motor Undervoltage Protection

Suggestion: .6 pu is too low since some motors will stall at .75 pu, others at .85 pu. Therefore, the answer is: It depends.

RE: Motor Undervoltage Protection


IEEE Std 399-1990 {obsolete} Chapter 9 Table 16 suggests a qualified 80% “at terminals of starting motor,” with 71% “at terminals of other motors that must reaccelerate.”  

The chapter may have applicable general material for this subject.  Current version of the “Brown Book” is IEEE Std 399-1997 Recommended Practice for Industrial and Commercial Power Systems Analysis
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources