Generator Vibration

Generator Vibration

Generator Vibration

(OP)
I did a vibration measurement in a Generator. I fix the active power (60 MW) and change the reactive power, varying the excitation current(reactive power). The amplitude (in velocity) at 1x decrease when I decrease the reactive power.

There are a explanation for this?
There are a mathematical model for explain it?
what are the relationship in the reactive power and mechanical vibrations?

RE: Generator Vibration

In very simple terms, you have a mechanical unbalance vector and an electrical unbalance vector by varying the reactive power you are changing one of the vectors and phase relationships.  When these vectors are in phase they are adding out of phase subtracting, hence lower vibration at one x.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources