Transfer data from one PLC to another.

Transfer data from one PLC to another.

Transfer data from one PLC to another.

(OP)
  

I have two plc's that basically control one machine. One is a AB 5/04 and the other is a 5/01. What I would like to know is if it is possible to move the data, say an input or an output from one plc to the other without actually running a wire from the output of one to an input of the other. Would it be like transfering data to a panelview by using a block transfer or can it be done at all, I'm not real sure. I realize if it can be done, I would have to upgrade the 5/01 processor to a 5/04. This is not a problem though. I would appreciate any help on this and thanks in advance.

KYLE

RE: Transfer data from one PLC to another.

The most straightforward way is to put handshaking PLCs on a network.
Panelview may be on the same network.
But be aware about such handshaking speed.
On DH485 you may have up to ~0.5 sec delay reading signals from one PLC to another.

RE: Transfer data from one PLC to another.

It is called messaging. Look in the help screens in RSLogix under MSG. I hade 4 5/04's talking to each other on one machine. I used the DH+ on the SLC's. There was also a touchscreen on the DH+. The only thing you have to do is set up each PLC and touchscreen with a unique node number and set the communications at the same rate. Once you can see each in RSWho you are ready.
If you have additional questions contact me.

Paul Thomas

RE: Transfer data from one PLC to another.

(OP)
Thank you Paul, forgot all about the MSG instruction.  In our apps. I've never used it, but looks pretty straight forward.  Thanks again.

Kyle

RE: Transfer data from one PLC to another.

I presume you probably upgraded to 5/04 by now.
The simplest method would be to use a 1747-PIC to interface from the 5/04 RS232 port to the 5/01 DH485 port.

The 5/04 RS232 port should be configured to DH485 protocol to say address 1. The 5/01 set to address 2.

The message instruction is simmple to use. Read the help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources