(OP)
A 11kV, 5000kW motor is provided with Differential protection. This motor has PF correction capacitors of 1.9MVAR coming within the zone of differential protection (due to the specific location of CTs).

This will mean that the PFCC current is not accounted in the differential scheme and thus requires the differential protection to be set less sensitive so as not to have tripping on the PFCC current that is going to appear as spill in the relay.

Any experiences / suggestions.

Thanks in anticipation.

RE: A 11kV, 5000kW motor is provided wi

Having been in the exact position that you describe, I would strongly suggest that the PFCC be moved such that the motor only is Diff. protected. Use other protection system to protect the PFCC.

RE: A 11kV, 5000kW motor is provided wi


IEEE C37.96 [and C37.99 and C37.103] do not seem to address the situation.  Given the typical 6-CT 3-relay installation, if the capacitor-tap location cannot be changed to outside of the stator-differential zone, the only solution may be to experiment with another set of CTs having as-close-as-possible electrical characteristics to the existing CTs—paralleled with the existing set at the differential-relay restraint-coil terminals.

A non-mainstream {more risky} approach, if the capacitors are ungrounded-wye-connected, may be to install something like a PT and 59G relay configured to supervise or inhibit 87M operation.
  

RE: A 11kV, 5000kW motor is provided wi

Simply add CT's on the PFCC tap and connect secondaries at motor side accordingly!

GH

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources