NEC 502.4(B)(4) requires all boxes and fittings to be "dusttight".  NEC 500.2 defines dustight as "enclosures constructed so that dust will not enter under specified test conditions".  It has a fine print note:

FPN: See ANSI/ISA 12.12.01-2000, Nonincendive Electrical Equipment for Use in Class I and II, Division 2, and Class III, Divisions 1 and 2 Hazardous (Classified) Locations , and UL 1604-1994, Electrical Equipment for Use in Class I and II, Division 2 and Class III Hazardous (Classified) Locations.

I would assume the ANSI/ISA 12.12.01-2000 deals mostly with instrumentation.  Looking at the scope of UL 1604-1994 (not wanting to pay over $500 just for the standard) it appears that UL 1604 applies mostly to equipment and not to enclosures just by themselves (although the equipment may be in an enclosure).

I would normally assume that a NEMA 4, 6, or 12 enclosure would be "dusttight", however the Hoffman Catalog in their NEMA standards table for applications specifically mentions "non-hazardous" and also states that for dust, lint, fibers, and flyings that they are not to be Class II.  

I have not seen any enclosures specifically UL 1604 listed.  MY QUESTIONS ARE THESE:  What do most people use for boxes and enclosures in a Class II, Division 2 location?  Does anyone know of enclosures specifically rated for Class II, Division 2 locations?  PLEASE NOTE THAT "DUSTTIGHT" IS NOT THE SAME AS "DUST-IGNITIONPROOF", WHICH IS A NEMA 9 CLASSIFICATION OR EXPLOSIONPROOF WHICH IS A NEMA 7 CLASSIFICATION.

RE: Class II, Division 2 Enclosures


It is possible that Hoffman doesn't feel that testing required to establish a NEMA type 7 NRTL listing is cost effective, or too great a liability if misapplied by the end user.
  
I believe there has been a similar problem with their NEMA type 12 and “JIC” enclosures substituted for type 3, 3R, 4 and 4X (!) duty.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources