Phase-shift current to match voltage shift through delta-wye XFRMR

Phase-shift current to match voltage shift through delta-wye XFRMR

Phase-shift current to match voltage shift through delta-wye XFRMR

(OP)
I am in need of a method and hardware to utilize the secondary of an existing CT circuit (wye connected) connected to the high side bus of a 12470/480V Delta/Wye transformer and have its phase and magnitude referenced to the low side.  In other words, I need a thirty degree phase shifting auxiliary ct circuit that does not interfere with the existing mains ct circuit.  

Does anyone have any experience in auxilliary CT circuits to accomplish this phase-shift.  Metering equipment will not allow a phase-shift to the 480V voltage reference, so the shift needs to take place on the current.  Please recommend what components you might have used and a configuration to accomplish this task.  

 

RE: Phase-shift current to match voltage shift through delta-wye XFRMR


Given “…auxiliary ct circuit that does not interfere with the existing mains ct circuit”…  ‘Cutting in’ to existing-component wiring where currently used for another purpose may initially be logistically cumbersome and a headache to maintain.  

Have you considered using a fully secondary-connected watthour meter with a programmable loss-compensation algorithm?  {One would need to use data from the power-transformer production test report, but the procedure seems a well-documented and accepted method.}  

Using auxiliary CTs in a phase-shifting [id est, wye/delta] arrangement where revenue transfer is involved may present special accuracy-class considerations; will always be difficult to test and likely unmanageable in securing against “modification,” particularly if any of the needed metering components are owned ‘by others.’
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources