Could anyone provide enlightenment on a problem I am facing with a Gas engine driven 11kV genset?
We have a gas engine, direct coupled (frame close coupled) to a 11kV 2/3rds pitch 3250kVA generator.
Connection is in start with a floating neutral.
Customers load lead connections are made in single steel wire armoured with the armour being connected at the switch end to ground only.
The set base frame is split in 2 halfs, one for the generator, the other for the engine. The generator base frame is connected to the common earth bus by a 50mmsq cable. There is cross earth bonding between the engine to base frame ( engine & gen on rubber AVM's), gen to base frame, engine base frame to generator base frame, engine to control panel & from control panel back to the common earth bus.

Under no load operation ( even with the load leads disconnected) we see a current flowing in the earth conductor, aproximately 6.5 to 15 amps.
Measure that with a slightly higher impeadance instrument & that value drops off quicky to somthing like 1.7A
The current is at 50Hz, & varies with the change of speed of the genset. The current amplitude varies with the change in generator terminal voltage.

There is significant stator field flux around the generator frame and a differential between drive end and non drive end of the generator in the regions of 182mV in open circuit condition.

My initial thoughts were capacitive coupling between the generator HV winding  the surrounding metal, generating a potential gradient, but can't balance that against the positive current flow through so many different paths
Any bright ideas people?


RE: Q - Spurious HV genset earth currents source

Just thinking out loud.
To generate a current you need
magnetic flux
conductor
relative motion between the two.
You said that you changed the RPM and the frequency changed of this problem current. Change the excitation on the field and see what happens.

RE: Q - Spurious HV genset earth currents source

Highly likely that it is circulating ground current caused by induction from the generator. The generator has a floating neutral and therefore no real reference to ground.
What types of instruments are you using to measure this current(you refer to using a 'slightly higher impedance instrument')? A clamp-on in typical for current measurement.

RE: Q - Spurious HV genset earth currents source


1-4% of nameplate current is probably of no significant concern, except for periodic checks to see that it does not evolve into something more serious.   

What is the purpose of isolating stator-neutral-to-ground connection at starting?  What happens to the subject current measurement at closing?  Is there a resistor involved?
  
Would you elaborate on "slightly higher impeadance [current] instrument"?
  

RE: Q - Spurious HV genset earth currents source

Suggestion: Contact the generator manufacturer for the generator capacitive charge current value. The current normally enters the system grounding calculation, either medium resistance or high resistance system grounding calculations.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources