Delta Secondary-Line to Neutral Relationship
What is the line to neutral mathematical relationship in a delta connected transformer secondary? As in, why is the "wild leg" voltage 208 volts, when the line to line voltage is 240 volts?
RE: Delta Secondary-Line to Neutral Relationship
A delta connected secondary of a transformer does not have a neutral connection.  Therefore there is no mathmatical relationship.  Each of the phases is floating with respect to the neutral.  If it where a Y connected, then the phase to neutral voltage would be  Voltage Line to line / Square root(2.
RickoZone - It is the square root of 3 - not 2,  in your formula.
The 208 V comes from taking line to line (240 V) and multiplying by the sine of 120 degrees, i.e. the phasor angle between the three phases.  My calculator gives 207.85 V as the actual value, rounded easily to 208.