BCT's on Recloser

BCT's on Recloser

BCT's on Recloser

(OP)
Hello.
What's the proper way of wiring a Circuit recloser used as a main protection of a radial feeder with BCT's on both loadside and lineside. The loadside BCT's are wired to the ground trip of the recloser. We need to a set of currents for monitoring purposes only (Ammeter Reading) and the other set is for protection (wired to protection relays). Is it better to have the loadside BCT's (with recloser ground trip) wired to protection relays or the other way around.
Thanks in advance.

RE: BCT's on Recloser

Suggestion:
Recloser (ANSI 79)
Designed mainly for overhead lines, used to clear
transient and semi-permanent faults, limiting user
service interruptions as much as possible. It consists
of resupplying power to the circuit that has been
interrupted by the protection after a time delay
required for isolation to be restored with the power off.
The number and type of reclosing cycles are variable
and can be adjusted by changing the settings.

Therefore, the BCTs should be used from that side where the semi-permanent faults are expected or probable.

RE: BCT's on Recloser

It's better to have the protection on the source side CTs.  This way, some faults within the recloser may be detected and cleared by the recloser.  It doesn't make a whole lot of difference, though, because faults within the recloser should be very rare and most would destroy the recloser instead of being cleared by it.

RE: BCT's on Recloser

Suggestion: The bus protection covers reclosers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources