I have a suitable formula for valve sizing, it requires data that is not readily available. Finding the fluid temperature at flow rated pressure is difficult to find, for instance sulfuric acid at 214.5 psig. Any help is appreciated.
Barry17

RE: safety valve sizing

The temperature comes from the process and the event that is causing the overpressure.  For example, if you are pumping the acid and are sizing the relief valve for the event of a valve being accidentally closed, the relief temperature is simply the normal pumping temperature.

For other relief cases, the analyses can be more difficult, what is the case(s) you are looking at?

RE: safety valve sizing

(OP)
TD2K, thanks for the reply, the application for these pressure relief valves is on railcar tanks, the formula establishes a flow which is sufficient to prevent catastrophic failure of the tank when a pool fire surrounds the tank. The tank exhaust to atmosphere through the PRV.
In the past,I have flow tested valves using air, pushing 20,000 scfm through the valve with the supply air temp at 520R and the temp at the nozzle being 475R. The flowing temperature is not the temperature of the product within the vessel.
Hope this help
Barry17

RE: safety valve sizing

Barry17:
You should get a copy of NFPA 30 "Flammable and Combustible Liquids Code". There is a formulas and a procedure to calculate the heat input due to a fire under a tank and the Pressure Safety Valve flow rate to vent off the vapor to keep the pressure below the vessel design pressure.

You can convert the heat input to a flow rate and conver the vapor flow rate to a equivalent air flow rate in Standard Cubic Feet per Minute or Hour.

Having the air flow rate SCFM or SCFH will allow you to look up a valve in the manufacturers catalog that will suite the need.

I have a spread sheet based on NFPA 30 which will do this calculation. My Email address is dlandis@tpdesignbuild.com
Email me your Email address and I will send you a copy.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources