Flow Rate Calculations
Hi guys,
I am new engineer how is working on replacing Fume Hood inside a lab with a new one.
I would like to know how to do the required flow rate so that I will select the blower accordingly. We are shooting for 100 f/min velocity through the face of the hood. I also I would like to know how to find the total static pressure.
The duct diameter is 10 inches.
Please advise me
Thank you very much
Please advise me
Thank you very much
RE: Flow Rate Calculations
Flow through hood
Q2 = 1.4 * P * D * V {cfm}
where
P = perimeter of tank or table below the hood {ft}
V = capture velocity (100 - 150 fpm)
D = free space above tank or table {ft}
When the hood is above a hot area, an additional flow Q1 of air or vapors is
formed.
To remove the vapours it is necessary that Q2 > Q1
For practical values Q2 = 1.2 * Q1
Calculation of Q1
Valid for D <= 3 ft
1) Hood above hot area without vapor generation
Q1= 5.4 * S * \3/--( h * dt1.25) {cfm}
S = Area hot plate { ft2}
t = temperature difference hot plate and ambient air {oF}
h = heigth hot plate above the floor {ft}
2) Hood above tank with hot liquid (vapor generation)
Q1= 290 * S * \3/--( h * G) {cfm}
S = Area top side of tank { ft2}
G = Vapor formation {lb/ft2/min}
h = heigth tank with hot liquid {ft}
Steven van Els
SAvanEls@cq-link.sr
i am constructing a natural drain here on my farm
the top of the drain is 12 ft wide
width of bottom is 2.7ft
gradient{fall} 420
depth of drain is 5 ft
can someon eplease calculate the flows in GPM when the water depth is 2ft,3ft,4ft
regards and awaiting a reply
John Lochhead
email is jlochhead@fencepost.com
You should start your own thread. In it you should also state the length of the channel you are constructing as well as whether it will be concrete, grass, gravel, dirt, etc.
I'm assuming that the depth you are concerned with is the depth at the very beginning of the channel (drain). If you supply the additional data I've described, the flow at the end of the drain can be calculated.
I'm also assuming that the dimensions (width, depth)of the drain are uniform from beginning to end.
Wayne
Checkout
http://virtualdesignbuild.com/DB/equip/ductwork.htm
for some information.
I would like to suggest to you that you provide plenty of isolation valves and locations for low point drains when you do have to isolate sections of piping. An old Maintenance Plumber told me that the first time you use a valve the valve has paid for itself.
Trying to plan for the future is almost impossible...... but something you might be able to do is this: Contact the people who will be actually using and maintaining the system... ask them where they would like valves / drains / filters / room for access or maintenance.....
You are very fortunate to have this opportunity to design this system and it sounds like you are working hard to make it a good one !
Good luck,