Is Fuel oil No. 2 generating a hazardous area acc. NFPA

Is Fuel oil No. 2 generating a hazardous area acc. NFPA

Is Fuel oil No. 2 generating a hazardous area acc. NFPA

(OP)
I need to design a storage tank farm with associated pump house. It should be designed according NEC/NFPA. Fuel is HSD No. 2 with a flash point of 70°C. 2 tanks with size of 20000qm. The pump house is located 20m away from tanks.
Is it required to design system in Ex-proof.

Pete M.

RE: Is Fuel oil No. 2 generating a hazardous area acc. NFPA

A liquid with a flashpoint of 70 degrees C is a Class IIIA liquid.  See NFPA 30 - 2000 Chapter 6, for distances from vapor sources to different types of electrics.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources