9 volts on a disconnected circuit

9 volts on a disconnected circuit

9 volts on a disconnected circuit

(OP)
Setup:

Strip Shopping Center with a 208-volt, three-phase circuit, Main panel metered by the power company, wiring trough fed by main panel and owner installed meters to provide services to tenants.

One tenant is a heath club with receptacles that serve treadmills.  On at least one receptacle, the voltage to ground when the circuit breaker feeding the receptacle is turned off is 9 volts.  Anybody care to venture a source of the problem?

RE: 9 volts on a disconnected circuit

Measured with a high impedance ammeter, induced voltages can be seen (certainly of the order of a few volts), depending upon load currents flowing in adjacent cables.  Perhaps use a lower impedance ammeter (or just select the Low Impedance option, if it's got one) and see what happens?

Brian

RE: 9 volts on a disconnected circuit

Suggestion: Longer power distribution runs or branch circuits may experience electromagnetically induced voltages. E.g. If a wire is run, as a laundry line, below high voltage transmission line, there could be enough induced power to heat an electric stove.

RE: 9 volts on a disconnected circuit

I agree with briand2 - using a high impedance DMM will pick up small voltages.  If you can get a analog meter, such as a Simpson 260, it will probably show zero volts.

RE: 9 volts on a disconnected circuit

Is it a three phase, four wire system? (Three phases + neutral, like the 208V implies) There could also be a voltage to ground if the neutral is not broken.

RCC

RE: 9 volts on a disconnected circuit

(OP)
I thought that there could be induced voltages but is 9-volts unusually high or normal?  Yes, this is a 208-volt, 3-phase, 4-wire sytem.

RE: 9 volts on a disconnected circuit

Nine volts does not seem high to me.  I've seen induced voltages of over 75 volts on a 120 volt system when measured with a high impedance meter.
Don

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources