VFD Supply Sag

VFD Supply Sag

VFD Supply Sag

(OP)
If a VFD's supply voltage sags for several seconds in the order of 10%-15%, and the VFD is previously at full load, rated voltage and 60 Hz speed, then what is the typical drive response. Will it shut down on low voltage or overcurrent? This is a common problem.

RE: VFD Supply Sag

Modula2

The answer to this question lies in how the drive is set up.  Most drives have both time and value thresholds that have to be met before it will shut down.

These should be user programmable so that nuisance shutdowns can be avoided.

RE: VFD Supply Sag

(OP)
I was expecting certain shutdowns to be fixed, for protection of the drive. And also, if the voltage only drops 10-15%, the slip should increase for the same torque, but input ac current should only increase by a comparable amount, and power stay about the same. So, I am not expecting an overcurrent nor overvoltage shutoff, unless there is something wrong with the drive.

RE: VFD Supply Sag

Sounds like a need for a voltage regulator or line conditioner.  Most microprocessors which are pre programed, and that have smaller capacitors for storage will not sustain in time lower voltages for many cycles.

RE: VFD Supply Sag

In most of the VFDs there is a feature called "Power Loss ride through" which usually takes care of such input voltage dips for few seconds. In this case the drive will continue to maintain the previous speed. But one should take care of the control supply part of VFD which, if provided from Input side, will again cause tripping of the drive (due to contactor/relay drop down). It is preferable to provide control supply from independent sources in such cases. In some cases, if the drive rating is almost matching the load, I mean to say that if there is not enough margin in the rating, there is a chance of drive tripping on overcurrent.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources