I want to install a hoist in my garage that is rated for 800 lbs maximum load.  The span across the garage is 13 feet.  What size I-beam should I be using?

RE: garage hoist i-beam size requirement

Pulling motors out of the race car again?  W8x15 should work quite nicely. It has a little extra flange width to pull off the bottom flange.  Provide some sort of restraints at the ends to prevent rotation of the beam.  That will be $125, please.

RE: garage hoist i-beam size requirement

hi,
  I have assumed you are using mild steel for constructing the hoist. After calculating the bending stress, and finding the section modulus, the I-beam should have the following dimensions.
TOP & BOTTOM FLANGE = 175MM
TOP & BOTTOM FLANGE THICKNESS = 10MM
MIDDLE WEB = 12MM
TOTAL DEPTH OF I-BEAM = 300MM

RE: garage hoist i-beam size requirement

I'm not aware of any American steel beam with the dimensions listed by hemanttht.  I am also not aware of any beam having a web thicker than its flanges. I-beams are not even produced in the US any more.  I recommend following Zulak's suggestion.  It's a commonly available beam with sufficient strength.

Also, don't forget to size the support columns at each end of the hoist beam.

RE: garage hoist i-beam size requirement

Actually an "I" beam (American Standard beam) works better for hoists than wide flange beams. The flanges are tapered in the inside which works better with the trolley wheels.

I would start with S6X TBD; assuming it is simply supported at the ends only and factoring lateral load due to impact (biaxial bending must be considered. I really do not think it is a good idea to post final sizes due to many unknowns. Hoist suppliers do recommend beam sizes to their clients (or at least the bottom flange dimensions that would work with their trolley wheels).

I would consult a local engineer to verify the results and also you need to ensure that the supports (masonry walls, columns etc. are adequate).

Good luck

RE: garage hoist i-beam size requirement

To check Deflection:
I = x in^4
Conservative simply supported
Deflection = (PL^3)/(48EI)
or
Fixed ends
Def = (PL^3)/(192EI)
where L is you span

Wouldn't go over .125 max deflection

RE: garage hoist i-beam size requirement

Analysis agreeds with Zulak's recommendation (thats why I gave him his star, sorry no $125).  If you wanted the other shapes then S8x18.4, or M10x9 will work using given 800# loading, 13' unbraced length and deflection of L/800.

Cheers

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources