I have a piece of equipment that has a LP
gas manifold inside the electrical control
panel (110 VAC) with the control relay. There is a seperator between the gas and the electrical sides inside the manufactured ss enclosure. Is this appropriate?
gas manifold inside the electrical control
panel (110 VAC) with the control relay. There is a seperator between the gas and the electrical sides inside the manufactured ss enclosure. Is this appropriate?





RE: LP propane with electrical
RE: LP propane with electrical
The separator provided inside an enclosure may not prevent the gas from migrating to the electrical equipment.
RE: LP propane with electrical
Even for field installations, there's no requirement that electrical installations near gas piping be XP. You can put an electrical outlet or lamp immediately adjacent to your gas meter in your house (actually, I'd recommend putting a lamp right next to the meter, it makes it much easier to read).
Maybe I'm missing the point of your question -- that's why I fired a few of my own back at you. If your question is only whether or not it's OK to put gas piping next to electrical stuff, well the answer is generally yes. Piping, valves, etc., should not leak when installed properly. If they do, then you have a world of problems.
Now, anything that could reasonably be expected to leak gas during maintenance or accidents are generally required to be XP. But your valve & piping do not typically fall into that category.