Swing Check Valve
Swing Check Valve
Can any body provide me a method for calculating the minimum velocity & pressure required to open and disc of a Swing Check Valve ?
RE: Swing Check Valve
All manufactors publish the cracking pressure for their style of valve. Velocity is not the a factor, although you do need flow to create pressure.
Because all valves are made different, you should contact the manufactor to answer your question.
I list assumptions I would use for general conditions below. I believe most swing check valves seat at 30 degrees or less so use this. You will need to assume some flapper geometry so use the internal diameter of the pipe size and figure the check pivot point is at the top of the circle.You will need to assume some bearing friction, I would assume zero.
You can then calculate based upon static pressures. I think you will find that you need a few inches of w.c. to open a swing check.
Regarding flow if the flow is small enough you will find there is almost zero pressure required. This is because there is little seating pressure for a swing check. A swing check only develops seating pressure from the hydraulic pressure of a return flow.
v = 45 x ( V )^0.5
v : velocity in (m\s)
V : specific volume of the fluid in (m^3 / kg)
I hope this helpful
Khaled Muhsen