Dewatering my Excavation
Dewatering my Excavation
(OP)
Say I have a rectangular excavation 120 feet by 80 feet by 20 feet deep (below grade surface) in the shallow water table in sandy soils (K = 10E-2 cm/sec). Sheet piling/deadmans are holding the sides of the excavation. Water table is at 10 feet bgs.
How can I estimate the pumping rate (gpm) for pumps placed in the dewatering wells?
As a simplified example (to see if I have any clue about dewatering at all), can I take the hydraulic conductivity (10E-2 cm/sec or 1.181 ft/day) and multiply by the area of the excavation bottom (9,600 SF) and convert to gpm units? I would then get 59 gpm (seems high for real world applications).
Does the head (10 ft above excavation bottom) or gradient come in to play in the calculations? How?
Now if I add wells, say 10 total wells along sides of excavation, how does this affect the calcs?
Trying to understand dewatering...
How can I estimate the pumping rate (gpm) for pumps placed in the dewatering wells?
As a simplified example (to see if I have any clue about dewatering at all), can I take the hydraulic conductivity (10E-2 cm/sec or 1.181 ft/day) and multiply by the area of the excavation bottom (9,600 SF) and convert to gpm units? I would then get 59 gpm (seems high for real world applications).
Does the head (10 ft above excavation bottom) or gradient come in to play in the calculations? How?
Now if I add wells, say 10 total wells along sides of excavation, how does this affect the calcs?
Trying to understand dewatering...





RE: Dewatering my Excavation
Based on the information you provided, 59 gpm does not seem like near enough pumping capacity for the excavation. I would strongly recommend you contact a geotechnical or dewatering engineer with experience in the geographic area where the project is located.
RE: Dewatering my Excavation
RE: Dewatering my Excavation
GeoPaveTraffic is right. You need to start where you want the water level to be, which will probably much lower below the excavation that you may think at this point. You also must be cognizant of area around the dewatering - ie do survey of existing structures.
RE: Dewatering my Excavation
You need a geotechnical engineer with good dewatering experience.
If the sandy soils are 80+ feet deep, then the dewatering system may not require too many wells. On the other hand, if you've got a clay layer at 30-40 feet, expect a LOT of wells.
Also be aware that the soils aren't uniform - so don't expect the bearing surface to be really dry unless you are willing to pay for redundancy - and a well or two within the excavation itself.