Deluge valve
Deluge valve
(OP)
Are there any restriction to use on-off valve instead conventional deluge valve? (Hydraulic signal actuated diapharm valve.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Deluge valve
RE: Deluge valve
If you are designing your own system that isn't required, you'd better be sure it will operate if anyones safety is at risk.
Listed deluge valves are tested and have to meet all types of standards related to reliability that regular valves don't have to meet.
Ken
RE: Deluge valve
You 'r right. I means process type on-off valves which are not in UL or FM list. However, in term of realiability, they can do the same or better then a deluge valve.
I understand that NFPA does not state that deluge valve have to be hydraulic actuated valve. Therefore, we could use process on off valve instead.
RE: Deluge valve
Is it permited to have a deluge system (open nozzles) with an on-off valve (a buterfly ULFM, hydralically and manually actuated, or an OS&Y gate valve for example) to supply the water?.
I have a case with open nozzles over an AST (tank) and we propose to control it with a UL-FM gate valve(OS&Y), we think the gate valve is simpler and the maintenance needs are less. The manual actuation is OK for the brigade. The system is NFPA 15 based, but we are not required for code compliance.