Propane gas sizing

Propane gas sizing

Propane gas sizing

(OP)
I have been told by the rep of a large propane supplier that propane pressure going into a building is usually less than 1lb. Well the tables provided in NFPA show sizing with either 10psi or less than 1lb. I just wanted to know how to go about sizing propane. If you have a 10 million BTU/h requirement for a warehouse what would be the pressure needed and the size of pipe needed?
please reply to sylore@hotmail.com

RE: Propane gas sizing

from what i recall, the tables in nfpa 54 are based on natural gas.  the natural gas capacities at various pressures and pipe sizes must be adjusted for specific gravity factors for propane.  nfpa 54 has another table of correction factors for specific gravity. sorry i can't recall what the factor is for propane, but it can easily be calculated through ASHRAE handbooks or perhaps through NFPA resources.

RE: Propane gas sizing

(OP)
NFPA 58 governs propane. I have used the tables for natural gas and for propane but speaking with a propane gas rep there seems to be some other tables that are out there not in the NFPA. I have developed a spreadsheet that calculates any of the following variables: downstream or upstream pressure, length of run, gas load, diameter of pipe. However this does not help me with the propane gas sizing inside buildings. If I get more info from the rep I will post it here.

RE: Propane gas sizing

The main objective of the pipe sizing is to make sure you have adequate pressure (which relates to flow rate) for the operation of the equipment.  Once you know your mass flow needed, and required pressure at the equipment with the longest pipe run, everything else will have to be regulated.  From what I have seen, much of the equipment contains a regulator on it, but it has a minimum pressure it will work at.  Based on your comment on a spreadsheet, I take it you know how to calculate pressure drop through the pipe.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources