(OP)
What is the applicable code for 200 psi fuel gas piping below an electrical power house with a concrete foundation and slab on grade?  The custody transfer meter is 40 feet outside the power plant fence.

Ditto for fuel oil piping at 50 psi in the same location?

RE: gas piping below buildings

transmission or distribution fuel piping?  likely distribution...

residential or industrial location - area classification is a consideration.

try international fuel gas code (public and residential applications) or asme b31.8 (likely choice).

make certain the pipe is protected from external corrosion.
-pmover

RE: gas piping below buildings

above 60 psig and in power plant service, some folks use B31.1 power piping for such fuel gas piping.

RE: gas piping below buildings

whoops!  ASME b31.8 is for tranmission pipelines.  had a brain spasm i guess.  sorry for the mix-up.
-pmover

RE: gas piping below buildings

I personally do not like to have fuel gas pipe running close to electrical room or house especially underneath.  If you have a leak, you will can fill up the room with explosive gas and your electical equipment is the ignition source for explosion.

RE: gas piping below buildings

Running a 200 psig fuel gas line beneath a building floor slab is very, very bad practice.  Any leaks and you have big problems.

I assume the fuel gas line is for a engine or turbine in the power house.  Run the gas line in a trench with grating or overhead.  Do not use floor plate as it traps the gas.

Be sure to adequately ventilate the room.  6 air changes are a minimum.

RE: gas piping below buildings

homerak, Just one question, "What happens when the foundations and building settles over time, which it will, can the gas and fuel oil lines support the building and equipment?" If the code doesn't take this into account, I would reject it. Good practice would be be to bring the lines up above grade just outside of the foundation line with an emergency block valve, run them into the building, then take them overhead as a header and provide valved line drops at point of use.

Remember, "Common sense and safe practice is the foundation and intent of all codes and standards."

Hope this helps.
saxon

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources