synchronous condenser mode

synchronous condenser mode

synchronous condenser mode

(OP)
I have the Beckwith M3425 relay protection on the 72MVA generator.  This gen can run as normal (producing power to the system) or it can run without the turbine (produce only VARS to the system for voltage support, synchronous condenser mode).  When doing the settings on the relay, I can program it (40,32,50/27,27,81u/o,50,51) for under normal mode.  What element should I need to change when the gen is operating under synchronous condenser mode?

Any help is appreciated.

Thanks

jt   

RE: synchronous condenser mode

The 32 element will be a problem, because without the turbine you'll need to drive the generator as an unloded sync motor, thus reverse power protection will have to be set above the power required to drive the generator, or disabled during "motor" operation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources