Chilled water buffer vessel size

Chilled water buffer vessel size

Chilled water buffer vessel size

(OP)
Does anyone have an equation that will calculate the required volume for a chilled water buffer vessel?

I use a 'rule of thumb' of 3 litres of fluid per kW of nett cooling, but I am after an equation that takes other variables into account.  Such as number of chiller starts per hour, flow rates, desired temperature fluctuation.......

Thanks for your help.

RE: Chilled water buffer vessel size

3 litres/kW cooling seems a bit low to me.  My experience is more like 7 litres/kW.

Brian

RE: Chilled water buffer vessel size

(OP)
Brian,

With Carrier chillers, you can use as little as 2.5 - 3.0 litres / kW for an air conditioning application.  If you need tight temperature control (such as a process application), then 7.0 - 8.0 litres / kW is my reccomendation.

Best regards,

Cooky

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources