air cooler equations

air cooler equations

air cooler equations

(OP)
i'd like to know the thermal design equations for air coolers, are these similar to shell and tube h.e. equations?
how could i kown how many motors (and their power) should i use for cooling

RE: air cooler equations

The GPSA data book also has a section on sizing air coolers.

RE: air cooler equations

ccorsi,

Go to http://www.hudsonproducts.com/download.html

They have free software that you can download that will size aerial/fin-fan coolers and fans. I have checked the  results against HTRI and other proprietary packages and the results are surprisingly good.  The U factor defaults are not always spot on but you can use your own if you have better ones available.

Regards,

Gunnar

RE: air cooler equations

ccorsi,

You answer your question a little more directly, the equations used for air-cooler are the same as for shell and tube exchangers on the tubeside only.  However, since they usually have fins on the outside of the tubes, you need a new set of formulae to calculate the extended surface area, fin efficiency, etc.

The Hudson program mentioned above works reasonably well, but uses fixed heat transfer coefficients (based on the bare tube area) as pointed out by gunnarhole. Remember that the tubeside coefficients are very much dependent on velocity, and therefore, available pressure drop.  If your situation requires very low pressure drop, you would probably want to adjust the heat transfer coefficient downward.

The question of motors and fans is related to the overall face area, rate of air delivery, static pressure, etc.  Most process coolers have two fans per bay, and approximately 40% fan coverage (fan area/face area).

RE: air cooler equations

ccorsi

speco is right. tube side equations are same as for shell and tube exchangers. the fin side calculations require determination of finned tube area, projected perimeter, equivalent diameter, flow area (which is based on face area). the subsequent methodology is same like shell and tube exchangers - caln of mass velocity, reynolds no. jh factor and ho though the curves used are different.
We can vary various parameters like tube size, fin OD, fins/inch. fin material, fin thickness etc to arrive at the most optimum design. We can also play around with tube pitch and row pitch to adjust the shell side pr drop.

hi-skore

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources