Magnetisation Current Calculation

Magnetisation Current Calculation

Magnetisation Current Calculation

(OP)
Hi all,

I have a transformer with the following information:
3150kVA, 3.3kV/0.415kV, Yd11, Z=6.5p.u.

The maximum magnetisation current at 0.02 seconds is 67420Ampere. How can I calculate this value as I have no idea about this.

 

RE: Magnetisation Current Calculation

The current that you gave is the infinite bus Fault Current calculated by I = (VA/(Sq3 * Vp))/Z

The Magnetising Current is the current to overcome the No-Load losses in the Transformer.

RE: Magnetisation Current Calculation

Applying a rule of thumb of 8 to 10 times the full load current of the transformer at 0.02 sec. provides satisfactory results in many applications.

This magnetizing phenomenon occurs during energization of  transformer and other apparatus. In the worst-case scenario, a value of flux approaching 300 per cent of nominal can be attained, thus causing appreciable saturation of the magnetic core and a massive inrush magnetizing current. The transient component decays rapidly during the first few cycles and more slowly thereafter. The damping is caused by the R/L factor, which is initially high due to the core saturation (L low) and decreases as the core becomes less saturated.
Suggestion:  search in this site and the Internet. There are plenty publications similar to the enclose samples:

Thread238-10885

http://www.sandc.com/webzine/111102_1.asp
http://www.sandc.com/webzine/012003_1.asp
http://pm.geindustrial.com/FAQ/Documents/T60/GER-4001.pdf

RE: Magnetisation Current Calculation


 you are talking about Inrush Currents or Magnetizing Currents?

RE: Magnetisation Current Calculation

I think it's fair to say that cuky was referring to inrush current, also sometimes called magnetizing inrush.  His comments on that topic were accurate.

I believe that steady state magnetizing current is typically in the range of 10% of full load current. It can of course be determined by measuring the primary current when there is no load on the secondary. Also can be determined from factory test data

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources