Isolated Phase service entrance conductors

Isolated Phase service entrance conductors

Isolated Phase service entrance conductors

(OP)
We had a project where the utility required isolated phase construction for a 2500a, 480V service.

What they wanted was that the parallel 7 sets of conductors had to be run separated by each phase to the service disconnect.

I never heard of this, and had to research the NEC to verify that was even legal.

The utility rep really did not have a good answer when I questioned the purpose. (they stated this way all three phases may not be lost if one leg faults and melts the conductor).

Does anyone know why this would bw an advantage to the utility?

RE: Isolated Phase service entrance conductors

It appears that you are referring to bundled conductors (IEEE Std 100 "Dictionary"). An individual conductor of a conductor bundle is called a subconductor. This is used frequently on shipboards instead of segregated or nonsegregated buses. Such installation withstands higher shocks than busbar buses. There are some disadvantages to this when it comes to capacitive charging currents and high-resistance grounded neutral system. The Utility may have a point since the 7 subconductor bundle  will cause the service or line to be more available / reliable. It will probably be more expensive to you but the high power supply availability may be preferred; especially, if any downtime is costly. What is the requested size of a subconductor?

RE: Isolated Phase service entrance conductors

(OP)
The "subconductors" were each 500kcmil.

thanks for the info.  I guess the utility answer was accurate after all.  They also noted a limitation of 25 ft and that conduits had to be PVC so that inductive heating affects would be minimized.  Special consultation had to be provided for longer runs.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources