(OP)
Article 400.7, NFPA 70, seems to prohibit the use of cable as a primary power feed, 600V, to industrial equipment, unless the installation is temporary.  Yet I can buy bus-drop cable, and the manufacturer specifically calls out NFPA 70, Article 368, and states that the cable is suitable for use as branch drop wiring from busways.  I cannot find Article 368 in my edition of NFPA 70, 1996.  Can anybody help clear up the apparent discrepency?

RE: Cable, Uses Permited

First:  Unless you're in a jurisdiction that is still using 1996 (wow!) put your 1996 copy into long-term storage and buy the 2002 edition.  If for no other reason than that 2002 was a major revision that moved the various Articles around big-time, and you'll have a hard time cross-referencing 2002 references against the table of contents of any older editions.

Anyway. . . .

In 2002, Article 368 is Busways.  In 1996, Busways was Article 364.

The key paragraphs for you are 400.7(A)(6)[same location & text in 1996 & 2002] and 368.8(B) [which is nearly identical to 364-8(b) in your 1996 edition].  So long as you meet the restrictions in 368.8(B)/364-8(b), you're golden.

RE: Cable, Uses Permited

(OP)
Yes I found out how outdated my code is, I haven't opened it since '98.  Thanks for you help, and for providing '96 citations.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources