Dead end / horizontal insulator strings

Dead end / horizontal insulator strings

Dead end / horizontal insulator strings

(OP)
All,

I've read the REA Bulletin 1724E-200 about design manual for high voltage trasmission lines. Page 8-2 on 8.2.3 "Deadends : In situations where the insulator string is in line with the conductor , the number of bells should be two more than what was used for tangent structure".

I try to find the reason of that additinal 2 bells for horizontal strings.

In my experince the vertical insulator is more prone to flash over than horizontal because the dirt on horizontal is easier to wash by rain than the vertical string.

Some one told me that for the practical reason, because the work on horizontal string is hard/complicated (its more complicated if you do it hot) than to work on vertical strings, so if one bell damage on horizontal we still can say it still safe.

please advise.

regards
Pitat

RE: Dead end / horizontal insulator strings

In a transmission line often conductor is routed down or around the insulator string in a dead-end or in a heavy angle structures.

These arrangements modify the field around to the insulator compromising the dielectric strength of the insulator string. Reinforcing this weak point with additional insulators is intended to maintain the minimum designed dielectric characteristic (BIL/BSL) with hope to minimize flashover in the event of surge overvoltage caused by traveling wave.

RE: Dead end / horizontal insulator strings

Lightning surges can double at deadends because of surge wave reflections.  The extra insulators increase the BIL (Basic Impulse Insulation Level).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.