EUROPEAN 220VAC DISCONNECT

EUROPEAN 220VAC DISCONNECT

EUROPEAN 220VAC DISCONNECT

(OP)
I'm in the middle of a discussion (read arguement) over the proper way to disconnect 220vac 1ph, in an electrical panel I'm designing to be installed in Italy. 220vac 1ph is being brought into my panel, which after going through a branch circuit protector, will be distributed to a series of dc power supplies. My question is, should I use a 2pole or single pole breaker for each of the power supplies? I'm thinking I need a 2pole breaker, but the other engineer believes I only need a single pole breaker. Won't I still have a potential of 110vac on the other leg if I only break one line of the 220? Could someone also point me to a place where I can find this info for myself?

Thanks,

Doug Greig

RE: EUROPEAN 220VAC DISCONNECT

u do need a 2 pole breaker
we had a similar application and we had to use a 2 pole breaker

RE: EUROPEAN 220VAC DISCONNECT

(OP)
Thanks for the responses and the link to the website. I guess for now we are going with a single pole breaker. But on the next panel that I will be repsonsible for I'm going to use 2 pole breakers.

Thanks Again.

-Doug

RE: EUROPEAN 220VAC DISCONNECT

Do you have two phases, or one phase and a neutral? All ungrounded(non-neutral) conductors should be opened together.

RE: EUROPEAN 220VAC DISCONNECT

Suggestion: If not overruled by local laws, rules and regulations, then the 220V single phase voltage system is supposed to have one circuit breaker, if the neutral is grounded (it may be dangerous to open the grounded neutral by the two pole circuit breaker, one pole for neutral and one pole for phase conductor), and if the neutral is ungrounded, then definitely a two-pole circuit breaker is mandatory.

RE: EUROPEAN 220VAC DISCONNECT

why is opening grounded neutral with a pole breaker dangerous

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources