I've been asked if we can connect to a building's existing fire storage water suction tank to provide water for a process need. I know it is not a good idea, but I'm looking for the specific code or NFPA requirement which does not allow this.





RE: private fire serice main
indicates:"Connections for use other than fire protection shall not be made."