Ground strap required on external cabinet doors?
12

Ground strap required on external cabinet doors?

Ground strap required on external cabinet doors?

(OP)
Was wondering if anyone knows if there is a code REQUIREMENT for ground-bonding straps ACROSS cabinet door hinges bonding the metallic door to the enclosure as oppossed to simply grounding through the hinges.

Any advice would be appreciated,

Thanks

RE: Ground strap required on external cabinet doors?

According to a major switchboard manufacturer, a ground strap is not a normal requirment by most customers and users, and that only West Coast utilities require a bonding strap from the door to main enclosure.

RE: Ground strap required on external cabinet doors?

2
Wiggie is correct in his statement.
Most doors on switchgear are bolted by metal hinges which provides adequate groung continuity so further strapping is not necessary.
Engineers often specify and insist the requirement not knowing that its just a folly

RE: Ground strap required on external cabinet doors?

Suggestion: Visit
http://www.ormec.com/motion/mktdocs/shldgrnd.htm
For: Use ground straps made from 1 inch (25 mm) silver tinned flat copper braid to connect the cabinet door(s) to the enclosure, the first sub-panel to the enclosure, and from each sub-panel to the next.

RE: Ground strap required on external cabinet doors?

2

Reliable continuity for fault currents and limited potential difference cannot be consistently achieved solely through door hinges—given routine paint, lubricant and corrosion.    
  

RE: Ground strap required on external cabinet doors?

I totally agree with 'busbar'.

In europe hinges would be classed as a "fortuitous" earth.  To ensure touch potentials are low whilst fault currents flow, a positive mechanism for earthing must be applied using a strap.  Hinges are not designed to carry current, so cannot be gauranteed.  I wouldn't touch it!!!!

For EMC protection, straps are no good, you must use an EMC gasket to totally seal the door, but that's another story/thread..............


RE: Ground strap required on external cabinet doors?

busbar and kevd,

What you say may be true, but it is not normal practice in the US to provide a bonding strap to panel doors.

The link given by jbartos is concerned with EMI protection of sensitive equipment and 300 MHz harmonics not safety for faults.

RE: Ground strap required on external cabinet doors?

As jghrist points, if it is not normal practice then why is it so!Is it that the above experts are correct and the whole of the switchgear industry blind.
The components (usually metering) rarely exceed 220v and backed up by a fuse not exceeding 10A, so where are these high fault currents coming from!
They never have bonding straps on washing machines/dryers, so does that make them dangerous!

RE: Ground strap required on external cabinet doors?

(OP)
RajT,

I think high fault currents are not the concern.  120V is enough to really hurt someone and is not so high as to be able to "drain" across a corroded hinge.  So if someone grabs the door, whammo, "Hello 120V".

Thanks for all the advice!

RE: Ground strap required on external cabinet doors?

In my experience, metal doors are bonded to the enclosure if instrumentation is installed in the door.  Otherwise, a bond strap is not needed.

RE: Ground strap required on external cabinet doors?

Re:  "As jghrist points, if it is not normal practice then why is it so!  Is it that the above experts are correct and the whole of the switchgear industry blind."

There's more than one way to skin a cat.  There's more than one way to ground a door.  Some are better than others, but many can be considered sufficient depending on the application.  Beauty is in the eye of the beholder.

RE: Ground strap required on external cabinet doors?

(OP)
What's with all the stars?

RE: Ground strap required on external cabinet doors?


The “West Coast” mention may be related to EUSERC metering standards for low- and medium-voltage metalclad sections that periodically require energized access by unsuspecting utility folks.  

No offense, but low-bid switchgear providers continue to keenly excel in outdoing their peers in what they affectionately call “doors,” and particularly “hinges,” that are (surprise) wishfully intended to remain serviceable for 30 years.
  

RE: Ground strap required on external cabinet doors?

Hey, just be happy the electrician put the door back on the last time he was in there.

RE: Ground strap required on external cabinet doors?

Peebee,
    I resemble and resent that statement!!!

RE: Ground strap required on external cabinet doors?

Hi Hipotential

I don't know the theorectical reasons why bonding jumpers are needed other than to provide safety to people and protect  equipment.As the previous threads indicate,it may be a lot of other reasons as well.
I have seen cabinet doors and transformer enclosures that show a distinct burnt mark around the enclosure bolt heads.At times these marks are in each bolt head on an enclosure.I do remember a time when we energized a new Power Tranformer and fire shot out around the bolt heads fastening the Secondary JB to the main transformer tub.
There were close to 50 , 3/8" bolts fastening the JB to the tub.Obviously added bonding was the answer.

GusD

RE: Ground strap required on external cabinet doors?

For what its worth, the military standard for Safety Design Criteria, MIL-HDBK-454A Guideline 1 recommends that hinges and slides not be used for grounding paths.  Its common pratice in MIL systems to include a ground wire between the cabinet and the door.  This is for personnel safety only, and not EMI/EMC as pointed out in an earlier post.

RE: Ground strap required on external cabinet doors?

Suggestion: My previous posting merely added to the previous postings that I essentially agreed with. The bonding doors; especially, when higher voltages are present is a prudent safety precaution, since the door may have higher potential against other conductive surfaces due to higher resistances in door hinges. Also, when contacted by live conductors, the door hinges may or may not necessarily trip the live conductor upstream protective device.

RE: Ground strap required on external cabinet doors?

Underwriters Laboratory Standards UL 1778 - UPS Equipment para 19.4 and UL 1741 - Inverters, Converters, and Controllers for Use in Independent Power Systems para. 20.3 state " A metal-to-metal piano-type hinge is useable as a means of bonding a door for grounding."

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources