Liquidtight flexible conduit
Liquidtight flexible conduit
(OP)
Can anyone tell (per NFPA) what is the maxium run length for liguidtight flexible nnmetallic conduit.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Liquidtight flexible conduit
|
RE: Liquidtight flexible conduit
Here it is as per the Ontario Electrical Safety Code - 2003'
Rule 12-1302(2)
Runs of not more than 1.5 m of 3/8 (12) trade size liquid-tight flexible conduit shall be permitted for the connection of equipment.
Intent for Rule 12-1302(2). Since the 3/8 trade size conduit is not recognized as a general-purpose conduit raceway method, we intend that it be restricted in use to runs of not more than 1.5 m for the connection of electrical equipment.
RE: Liquidtight flexible conduit
RE: Liquidtight flexible conduit
RE: Liquidtight flexible conduit
That should have been 356.10(5)which refers to support 356.30 : every 900mm (3ft) and within 300mm (12") on every box,fitting,etc.
RE: Liquidtight flexible conduit
Sorry for the confusion.
Dave