(OP)
Looking at measuring harmonic currents and voltages in a 22kV system. The plan is to use the output of the existing CT and VT. How much will these transformers(especially the VT)suppress the individual harmonics that we are trying to measure? What options are could be explored to do the measurements without these transformers?

RE: harmonics measurement

The C.T and V.T should suppress the individual harmonics only when they will be under saturation condition or higer then the 50th harmonics.
I would like to know if their is anther option to do it.

RE: harmonics measurement


Very informally, with their reduced inductance, CTs have better high-frequency response than PTs.     

There are passing comments on the matter in IEEE publication 90EH0327-7-PWR (1990), Nonsinusoidal Situations: Effects on the Performance of Meters and Definitions of Power
  

RE: harmonics measurement

The bandwidth of instrument transformers depend a bit on design, but in general the following applies:

For CTs, you should get pretty linear response up to about 2 kHz or so.

For VTs, they can vary substantially by voltage class and design, but they generally will only be linear up to between 500 Hz and 1 kHz.

If you want to measure harmonics only, then for the voltage, you could try a resistive divider (I believe S&C makes one at 25 kV). If you need voltage for metering or relaying as well, then you probably need to use a VT for metering and relaying and a resistive divider for harmonic measurments. If you have a high-end meter (like from PML), then it should have seperate inputs for power and harmonics.

Your best bet is to ask the manufacture for the harmonic performance, because as I mentioned, there is great variation between designs and voltages classes.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources