Parallel conductors DC system

Parallel conductors DC system

Parallel conductors DC system

(OP)
I need to feed a DC motor armature with about 1650 amps.I plan on using (5) 500MCM conductors per pole. Can I run (2)pos conductors and (2) neg conductors plus ground in two conduits and (1) pos conductor and (1) neg conductor plus ground in a third conduit?

RE: Parallel conductors DC system

Suggestion: It can be run:
Conduit # 1:  +500MCM x 2  -500MCM x 2 and Ground
Conduit # 2:  +500MCM x 2  -500MCM x 2 and Ground
Conduit # 3:  +500MCM x 1  -500MCM x 1 and Ground

RE: Parallel conductors DC system

Per NEC Article 250.122,
Grounding conductor must be the same size in all conduits.
250MCM for 2000 amp overcurrent devise.
Per NEC Article 310.4 Parallel conductors.
Per NEC Article 310.15 Ampacities.
Try 2-4" with 6-500MCM and 1-250MCM Grounding

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources