Can I tie into a 277 volt lighting circuit and transform down to 120 volts and feed ceiling outlets used for promotional purposes?

RE: national electrical code

Probably.  The transformer needs to be accessible and you must provide transformer protection and 120V circuit protection in accordance with the NEC.  This will require additional circuit breakers or fuses on the secondary side of the step-down transformer.  You can't really rely on the 277V breaker back in the panelboard to protect anything downstream of the transformer.  

RE: national electrical code

Slight correction, dpc:

Secondary overcurrent protection is not required on 1-phase 2-wire transformers.  See NEC 240.4(F) for details.

RE: national electrical code

peebee,

You're right, provided primary protection is sized according to this paragraph.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources