Generator reactance tolerances

Generator reactance tolerances

Generator reactance tolerances

(OP)
Hello,

I'm currently performing a short circuit study.
For this calculations, the generators direct-axis subtransient reactance is required. At this stage, I know the expected value of this reactance (unsaturated & saturated value), however I've also to apply tolerance according to ANSI C50.10.

Could someone provide me with tolerance defined in ANSI C50.10. Thanks in advance.

RE: Generator reactance tolerances

Suggestion: Please, would you be more specific about those tolerances defined in ANSI C50.10. This is not exactly a tolerance citing standard.

RE: Generator reactance tolerances

IEC is +/-15%.  It is usually practice to take the -15% which gives the worst case reactance after factory test and gives the maximum possible current.

I cannot imagine ANSI is much different.

RE: Generator reactance tolerances

(OP)
jbartos, kevd, thanks for your replies.

jbartos, my concern is I don't have the American Standards defining the applicable tolerance on the expected value of the direct-axis subtransient reactance (I assumed it was ANSI C50.10, but maybe I'm wrong).
As suggested buy kevd, I've used the IEC tolerance (-15%), but I've to perform my calculations according to American standards. So this is still an issue.

RE: Generator reactance tolerances

It should not be an issue if you state in your calculations all assumptions made.

RE: Generator reactance tolerances

Suggestion:
1. IEEE Std 115 test generator for short circuit parameters. However, the Xd" accuracy is often specified in the generator spec, e.g. plus minus 10%
2. Visit
http://www.hq.usace.army.mil/cemp/e/Et/emergenc.pdf
and check with generator manufacturers
3. Military standards requires for the Xd" measurement that the generator speed tolerance is plus minus 1% and measuring accuracy is plus minus 0.5%.
See
MIL-STD-705C
24 April 1989
SUPERSEDING
MIL-STD-705B
26 June 1972
MILITARY STANDARD
GENERATOR SETS, ENGINE DRIVEN
METHODS OF TESTS AND INSTRUCTIONS

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources