Hi All,

When you are checking the compaction ratio of sleeves or lugs, which of the following do you use?
1)  Always use the solid cable diameter dimension, as the conductor size
2)  Use the type of cable you are using, as the conductor size.

For example if I have 750 kcmil compact cable. Do I use the solid cable diameter of 0.866" or the compact cable diameter of 0.908"?

Thanks

RE: Simple Connector Compression Question?


Use compression fittings and die based on cable size and stranding exactly as specified by the connector manufacturer.  The solid dimension would be a misapplication, and likely an undersized connector that may not fit over the stranded conductor of equal circular-mil size.
  
Using only overall conductor OD for connector sizing is not intended by the connector manufacturer, and may give unacceptable termination/splice performance, as well as voiding product listing.    
   

RE: Simple Connector Compression Question?

(OP)
Thanks busbar,

Just to clarify the question I had though.  I am referring to the Compaction Ratio when the connector is crimped over the conductor.
Compaction Ratio = ((Conductor Area + Connector Metal Area) /Die Size)-1
Should be between 5-20%...

If too small, the conductor won't be well pressed and therefore heat up too much.  If too large, birdcaging of the cable or some other mechanical defect can be introduced.

So, would I use the solid conductor area no matter the type of cable as it would be crimped?

Thx

RE: Simple Connector Compression Question?


If I understand the situation correctly, I would let the connector manufacturer worry about compaction ratio, and base the installation on their recommendations.  This should eliminate concerns about the too-small/too-large performance.  
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources