Why is there not a 90% gas fired heating and cooling packaged units.  If there is a unit, where do I find it?

RE: 90 percent gas furnaces for packaged units

What the heck does this question want to ask ???

RE: 90 percent gas furnaces for packaged units

90% of what?

I assume you mean a 90% HHV efficiency.  Most smaller units that meet the 90% HHV efficiency use pulsed combustion and partial condensing of the fluegas. 2 issues with this are (a) noise from the pulsed combustion and (b) stack corrosion and required fan head to pressurize the stack to exhaust the fluegas. For smaller units a CPVC stack might meet building codes, but for larger units it might not meet fire code, and a pressurized exhaust is a risk to occupants.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources