Does anyone know where I can get information on General Electric Reactrol controllers?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: GE Reactrol
Quando Omni Flunkus Moritati
RE: GE Reactrol
It is a reactor type controller. Maybe the controller was not built by GE, could be mistaken. The application is electrical heating element (current?) control for an industrial oven application. It was installed in the 50's. The oven control panel was built by GE.
The name of the controller is "Reactrol". It is connected to saturable core transormers that are in series with the heating elements. The heating elements are configured in a delta connection. I am fairly certain that the transformers control the current in the heating elements, thus the heating power.
RE: GE Reactrol
Quando Omni Flunkus Moritati
RE: GE Reactrol
I have more general information, but still not too much technical detail. The Reactrol controller was built by GE. Do not have an exact year. The reactors consist of two AC coils in parallel, with the reactors in series with the load. Around the core of the reactor is a DC winding which is used to vary the reactance (and current) through the reactor. Interesting arrangement, I would like to learn more but can not find any resources in my textbooks or on the internet. I am especially interested in the power factor and efficiency of this system as I am sure there is significant energy savings by replacing with SCR control.
RE: GE Reactrol
gc — not sure if this will help, but a subject that may point to more information is arc welding. At one time saturable reactors were popular for welding-current control. They allowed a relatively small DC current through a potentiometer {like in a foot pedal) to control a much larger AC {or DC when rectified} current. That may have been where the term ‘magnetic amplifier’ came from.
As far as the SCR suggestion, I think maybe some readers though you were looking to replace a damaged or otherwise too-expensive-to-fix system. I think SCRs upstaged saturable reactors as soon as their capabilities commercially reached that point.
RE: GE Reactrol
RE: GE Reactrol
http://www.warnerpower.com/technical/powerfactor1/power_supply_development.html
I still think you should consider SCR control.
Quando Omni Flunkus Moritati
RE: GE Reactrol
Probably will consider replacing with SCR controller in future. Thank you all for the information.