Calculating the Maximum Floor Load

Calculating the Maximum Floor Load

Calculating the Maximum Floor Load

(OP)
Could you tell me specificly how to calculate the maximum floor load for the following type of floor:
Oak wooden floor of 1 inch thickness sitting on latts of approximately 3-5 inch square in thickness, and in turn sitting on 2-3 foot of stone (or up to one metre)?

RE: Calculating the Maximum Floor Load

Hi:

You'll need to describe your floor a little better.  

What are latts?
What does 3-5 inches square in thickness mean?  All of this sits on stone which is 2 or 3 feet thick?  Are we to assume the stone is based on terra ferma or is it sitting on something else?

RE: Calculating the Maximum Floor Load

I think he is talking about what load he could put, drive, store on this floor.

RE: Calculating the Maximum Floor Load

(OP)
By latts, I mean joists that are circa 3-5 square inches in size.  It is on the first floor of a building.  This floor is approximately up to 2 metres thick and made from stone and bricks.  The rooms are small in diameter, and the walls on the first floor sit directly above those on the ground floor.  They are approximately up to one metre in thickness.

RE: Calculating the Maximum Floor Load

What is holding up the actual floor? Right now you have about 6.5 feet of stone, rock, brick with a weight of 120 pcf and an additional 7-9 psf for the oak and 'latts'. The total wieght of 1 square foot of that floor is around 790 pounds psf now. that is a large load in itself.

RE: Calculating the Maximum Floor Load

Lorraine6,

I think we are all having difficulty imaging the floor framing system you describe.

Is this floor system directly supported on the ground, or is is suspended?

RE: Calculating the Maximum Floor Load

This is possibly one of the main reasons drawings are the best form of providing construction information!

RE: Calculating the Maximum Floor Load

(OP)
The floor would be suspended.  I don't have the equipment to send photos, drawings, or images - sorry.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources