Kindly advise what should I do if for some reason I have to cut and replace our first valve on the ASME boiler boundry. What does code say on the operated boiler with that case, thanks.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Boiler Hydrotest
Thread794-42433
RE: Boiler Hydrotest
Thread 794-42433 is talking about replacing PRV, not mentioned weather weld connection or flange connection type of PRV. I am more interested on the cutting weld job, which I understood that will require hydrotest, but I am not 100% sure. Is anybody could help me out. Thanks.
RE: Boiler Hydrotest
This action would be classified as a repair. If you desire to continue having a boiler that complies with and is certified to the ASME code, then the repair should be accomplished in accordance with the NBIC ANSI/NB-23, Part RC Repairs And Alterations Of Pressure Retaining Items.
The boiler will require a pressure test and possibly some NDE depending on material and operating conditions. A company in possession of a current and valid NBIC “R” stamp should be able to detail the specific requirements.