British Standards versus NEC

British Standards versus NEC

British Standards versus NEC

(OP)
I am reviewing an existing installation in the U.K. Presently there is a 1000 amp feed to an MCC. Prior to entering the feeder breaker of the MCC, there is a cable tapped off the feeder and services a 160 amp breaker which in turn acts as a main to a distribution panel. The tap is sized for the ampacity of the 160 amp service. In the NEC world this would qualify under the 25 foot tap rule. Does anyone know if there is a "tap" rule in the British Standards similar to that in the NEC?
Any assistance would be appreciated.

RE: British Standards versus NEC

For the NEC, it really depends on the length of tap.  How long is the tap?

Mike

RE: British Standards versus NEC

(OP)
I realize that the length of the tap is a qualifier in the NEC, my question was if this same type of tap rule exists in the British WIring Regulations. Nonetheless the tap in question is around 25 feet.

RE: British Standards versus NEC

Sorry,

I mis-read your post.

Mike

RE: British Standards versus NEC

Becrez,

If you are working in UK, suggest you get a copy of IEE Wiring Regulations (BS 7671) ISBN 0 85296 988 0 available from sales@iee.org.uk.

Regulation 473-02-02 says that
'The ... protective device may be placed ... at a point on the load side [such that the distance shall]:
i) not exceed 3m in length, and
ii) ... reduce to a minimum the risk of fault ...
iii) ... reduce to a minimum the risk of fire ...

Cutting through the bull, my interpretation is that this is like your NFPA70 para 240-21b for the 10ft length ONLY.  There is no general provision for taps of 25ft and above in the same way that NFPA 70 does.

Hope this helps,
RAC.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources